Currently, we are in the process of wiring a 90+ condo building. The service(120/240V @ 2000A) that will supply this building is taken from a larger piece of EXISTING equipment downstream(4000A). The main panel serviced by this 2000A consitits of 2 switches (1600A and 1200A) that feed the meter banks. Each meter in the stack(4 per stack) in the banks contains their own disconnect (a meter main stack ).
I am confused by this picture of Mike's:
The design of our layout is similar to the picture, in that we have:
- a seperate ground to building steel
- parrallel feeders in conduit (4 wire, no EGC)
- a bus connection(s) instead of a through
The risers to the individual units consists of 2 ungrounded conductors, 1 grounded conductor and 1 EGC.
Am I to understand that EACH of the 90+ meters MUST have a neutral to case connection?
I can gather images of our installation if need be.