Only the part that impedes the opening of the cover is in violation IMO. I personally don't like the location of this equipment but don't feel it can be called an NEC violation either.boy, these posts move too fast lol......that phone system needs to go somewhere else. I don't think its a dedicated space violation, but a working clearance violation.
That is what I disagree with. I think it means the equipment must be associated with the panel install not covered in the NEC. If that is what they wanted then they should have said any equipment covered in the NEC is allowed.
If the phone equipment plugs into a 120 volt receptacle supplied by the panel does that change everything?
If you had 277/480 volt panel and 120/208 volt equipment similarly installed above such panel is that much different?
And if this equipment extends no more than 6 inches forward of the panel it can be right on top of the panel even if the top of panel is only 36 inches above the floor.This is, as David said, a 110.26(A) issue and not a 110.26(F). Compliance with 110.26(A) would not be difficult or take a lot of time. They only have to get the bottom of the phone equipment to 6'6".
Again IMO telephone equipment doesn't belong there, but according to NEC I believe it is electrical equipment and not much can be said to cite code violations here - aside from the part that interferes with opening the panel.