Confusion on Ground fault protection for equipment.

Status
Not open for further replies.

Ingenieur

Senior Member
Location
Earth
you have 3 ph ct
a neut ct
and no bonding gnd-neut

perhaps the neut will carry current, ie unbalanced
so to detect a gnd fault they compare the 0 seq to the neut
if 0 seq - neut > 0 must be gnd fault
???
 

Ingenieur

Senior Member
Location
Earth
is the neut ct before or after the tie referenced to the source
would a frame gnd fault bypass the neut ct on its return to the X0?
 

Ingenieur

Senior Member
Location
Earth
The neutral Ct is between the system bonding jumper and the load neutral buss. Thus a L-Gnd fault doesnt go thru the CT on the way back to XO = trip.

so if sum(phase i's) + neut i not = 0 must have gnd fault
same as 0 seq - neut > 0 then gf

if you landed gnds on neut then phase + neut + gnd always = 0
 

Ingenieur

Senior Member
Location
Earth
I concur. I didnt see the neutral CT at first so I couldnt see what difference it would make - not to mention didnt quite get how the GFP would work :dunce:

it is not the usual method
typical is on the gnd tie as you said

but this allows current metering, ph relaying, etc
looks like v is measured also
do you have a pic of the relay section/cabinet?
 