you have 3 ph ct
a neut ct
and no bonding gnd-neut

perhaps the neut will carry current, ie unbalanced
so to detect a gnd fault they compare the 0 seq to the neut
if 0 seq - neut > 0 must be gnd fault
???
 
is the neut ct before or after the tie referenced to the source
would a frame gnd fault bypass the neut ct on its return to the X0?
 
The neutral Ct is between the system bonding jumper and the load neutral buss. Thus a L-Gnd fault doesnt go thru the CT on the way back to XO = trip.

so if sum(phase i's) + neut i not = 0 must have gnd fault
same as 0 seq - neut > 0 then gf

if you landed gnds on neut then phase + neut + gnd always = 0
 
I concur. I didnt see the neutral CT at first so I couldnt see what difference it would make - not to mention didnt quite get how the GFP would work :dunce:

it is not the usual method
typical is on the gnd tie as you said

but this allows current metering, ph relaying, etc
looks like v is measured also
do you have a pic of the relay section/cabinet?
 