Connect appliances from Europe in the US

Merry Christmas
Status
Not open for further replies.
Amor Electric

Amor Electric

I liked mdshunk answer.
But I believe that if the appliance is not a UL and something happened they can go after me
 
Last edited:
mpd said:
iwire

our administrative code requires it to be listed for for use in the US, if he was getting a permit for that grill, I would require the grill to be on site for final inspection

Thank God I do not live there. The permit would be for a receptacle, not a grill. That is crazy, really is this still America? :roll:

Do you hang outside homes looking for non-listed home appliances?

You do realize standard NEMA motors are not UL listed, how do you deal with that?
 
gilamor said:
The circuit should be 15AMP.

Is the Grill less than 1440 VA?

Did you read NEC 210.6(A)?

If its less then 1440 VA the NEC will not allow it in a dwelling unit unless it is 120 volt.
 
iwire
By the way in most areas inspectors will accept listings other than UL

funny you should say that, I bought a case of gfic outlets on line ( great price) Local Inspector was there and picked up the box wrote down the UL number. Several ays later he notified me that the UL# was a candaain # not USA, Is there anythin in the NEC that says it has to to UL listed in the usa?
 
iwire

no I do not hang outside of peoples homes, the OP was a receptacle for a grill,
the OP said it was not listed in US, and if a contractor dropped of a permit for a receptacle I would ask what is it for, is that so out of line, since you know it all what questions would you ask for a contractor dropping off a permit for a receptacle, or would you just sign it off and issue it and deal with it in the field,
 
gilamor tell your customer to send it back to Europe, I would not get involved in that liability
 