Connect bus duct sections with cable

andrew1

Member
Location
Indiana
Occupation
Specifying Engineer
Would it be okay to connect two bust duct sections with cable? The bus duct and cable conductors would have the same ampacity ratings.

Design would be:

Overcurrent protection----bus duct----tap box----cable----tap box----bus duct

I have looked through the NEC and did not find anything contradicting that this is acceptable. Does anyone have any experience with a similar design or knowledge of its acceptance?
 
Not a problem. Have done this many times over the years to span expansion joints, change elevation, or provide an offset.
 
  • Like
Reactions: ron
I agree with Jim. We've using the bus duct for accessible vertical portions of the run and conduit and wire for horizontal portions where it was inaccessible after installation.
 