110617-1458 EDT
jaggedben:
Others contributed much more than I did. I was simply asking questions to ferret out the road blocks. iwire provided the specific code parts that set the limitations.
I have some more questions. Are the feeder wires from the main panel to the subpanel adequate for the 60 A backfeed? The worst case I believe is with a capacitor on the subpanel drawing 60 A of reactive current, and the inverter providing 60 A of unity PF current. This results in an 84 A current in the feeder. No information has been provided on the feeder wire rating, maybe something is implied about its rating.
Can the feeder wire to the subpanel be moved from a load breaker on the main panel to a line side tap thru an inexpensive breaker box?
All these questions inter-relate economically with the cost of a separate line from the inverter to the main panel area.
When DTE was doing their Solar Currents program they required the inverter to pass thru its own meter back to their feed. I do not know if DTE requires this on all the grid-tied inverters to their system, or just for the Solar Currents program.
.
jaggedben:
Others contributed much more than I did. I was simply asking questions to ferret out the road blocks. iwire provided the specific code parts that set the limitations.
I have some more questions. Are the feeder wires from the main panel to the subpanel adequate for the 60 A backfeed? The worst case I believe is with a capacitor on the subpanel drawing 60 A of reactive current, and the inverter providing 60 A of unity PF current. This results in an 84 A current in the feeder. No information has been provided on the feeder wire rating, maybe something is implied about its rating.
Can the feeder wire to the subpanel be moved from a load breaker on the main panel to a line side tap thru an inexpensive breaker box?
All these questions inter-relate economically with the cost of a separate line from the inverter to the main panel area.
When DTE was doing their Solar Currents program they required the inverter to pass thru its own meter back to their feed. I do not know if DTE requires this on all the grid-tied inverters to their system, or just for the Solar Currents program.
.