sergiyny
Member
- Location
- Brooklyn, NY
I have (2) 100 amp, 3ph, 480V outlets installed in floor. From each outlet there is 1" conduit concrete encased running to each it's own junction box. Those 1" conduits can take only 3#3 awg wires. The panelboard from which (2) 100 amp outlets will be powered, it is 400 ft away. Because of the voltage drop I need to go with bigger wire size, in this case its 2/0 and it cannot be installed in 1" conduit. Now here is my question, I want to install 2" conduit and run 3#2/0 in it to the junction box and from there I need to go with 1" conduit and 3#3. Can I connect #3 and #2/0 together? If it's not allowed, what are my other options?