richwaskowitz
Senior Member
- Location
- Shelby Twp. MI, near Detroit
Let me stop being general and spell it out.
We are a controls systems integrator and we design industrial control panels. We are also a UL panel shop so we put UL labels on our panels. We, the designers, utilize the methods found in UL508A SB to determine the SCCR of our panels. We take advantage of the provisions in part SB to improve what would otherwise be a low rating when we can. Sometimes however, at the customer's insistence, we have had to include in a panel a VFD which has no published SCCR. That means it defaults to the value in table SB4.1. For a drive up to 50 hp, that means 5 kA. This can bring the entire assembly (panel) down to 5 kA. So, we do our due diligence and put a label on the panel indicating the 5 kA SCCR. What do you guys do with it when it shows up on the floor and you know the bus can deliver 45 or 65 or more kA?
I guess what I am getting at is that I believe that I need to advise our management against this practice and set some minimum rating or target such as 45 or 100 kA for our designs in cases where the end-user does not specify a minimum. In the case of the VFD with the low rating, I suppose we will have to decline the job.
We are a controls systems integrator and we design industrial control panels. We are also a UL panel shop so we put UL labels on our panels. We, the designers, utilize the methods found in UL508A SB to determine the SCCR of our panels. We take advantage of the provisions in part SB to improve what would otherwise be a low rating when we can. Sometimes however, at the customer's insistence, we have had to include in a panel a VFD which has no published SCCR. That means it defaults to the value in table SB4.1. For a drive up to 50 hp, that means 5 kA. This can bring the entire assembly (panel) down to 5 kA. So, we do our due diligence and put a label on the panel indicating the 5 kA SCCR. What do you guys do with it when it shows up on the floor and you know the bus can deliver 45 or 65 or more kA?
I guess what I am getting at is that I believe that I need to advise our management against this practice and set some minimum rating or target such as 45 or 100 kA for our designs in cases where the end-user does not specify a minimum. In the case of the VFD with the low rating, I suppose we will have to decline the job.