jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
In my case, I really don't care all that much. It's a bit simpler/cheaper just to run the EGC back to the service rather than establishing a new GEC on the other side of the split and bonding it to the existing electrode, but it's not a big deal. A case for compliance can be made either way..
I've come around to view it pretty much the same way, which is why I didn't propose that change to the service definition last time around.
There is one type of case I've seen where it really does make a difference, and could really suck if you didn't get on the same page as your AHJ before you started install. That's where your (large) inverter doesn't require a neutral. In that case you'd like to argue that the PV disconnect is not a service disconnect so that you don't have to bring a neutral to it according to 250.24(C). Or at least you'd like your AHJ to accept that it's safe regardless of what terms you use. The neutral itself could cost a lot of money if it's large and long, but what would cost more is if you made your conduit too small before asking your AHJ if they would require it.