Connecting low voltage transformers

Status
Not open for further replies.

K_Mark

Member
I have run into an interesting situation. I am helping re-design an office building into a dormitory. This requires about a 3,000-amp switchboard at 120/208, 3 phase. We are stepping down from a 277/480 volt system. Instead of using one large dry-type transformer, we were looking at using three smaller dry-type transformers. Has anyone ever seen this done? What does the code say about it? How would you connect them? On the secondary side I figured you could just take the feeder from each transformer to the switch board. But I might be wrong about that. I was thinking that each transformer should have it's own feeder on the primary side. Any ideas or comments would be appreciated.
 
Are you going to have three seperate switchboards? Or, are you intending to parallel the three transformers to feed one switchboard?
 
I am having a hard time visualizing any benefit from paralleling transformers. Most smaller "off-the-shelf" transformers are probably not built with consistent enough impedances to reduce load splitting problems.

I would be interested in why you are thinking of this method instead of a standard 1000KVA unit?
 
I assume that the building has several floors. If so, I would keep the 277/480 service and install a 120/208 transformer on each floor.
What do you have except Lts and receptacles?
 
K, without knowing more details, I'd suggest each transformer have its own feeder and OCP, and have each feed a separate panel.
 
Thanks everyone. It wasn't my project and I just wanted to get some other people's perspectives. The gentleman I am working with saw a riser diagram from the existing building and wanted to copy what they had done. But there is more to it than he realized. I appreciate all the input.
 