Connecting two zero sequence CT in parallel

Status
Not open for further replies.

Ingenieur

Senior Member
Location
Earth
And allow the other supply to keep on supplying.


he would have to move the ct to the load side of cb a and b
leaving them on the 1 to a/b feeder would be an option, but not a good one
and still not protect the 1 to a/b feeder

so if the fault was beteeen 1 and a or b it would go undetected
he wants to protect the feed from 1 to a/b
 

Besoeker

Senior Member
Location
UK
he would have to move the ct to the load side of cb a and b
leaving them on the 1 to a/b feeder would be an option, but not a good one
and still not protect the 1 to a/b feeder

so if the fault was beteeen 1 and a or b it would go undetected
he wants to protect the feed from 1 to a/b
Yes, obviously they would have to fitted on the load side of a and b.
But, in my opinion, that would be a better option. Especially if they are not yet installed.
 

Ingenieur

Senior Member
Location
Earth
Yes, obviously they would have to fitted on the load side of a and b.
But, in my opinion, that would be a better option. Especially if they are not yet installed.

that would not protect the 1 to a/b feeder which appears to be his intent

his question: can he parallel the 0 seq ct's to drive 1 relay to trip cb1?
yes
perfectly acceptable, std practice, as noted in the white paper
 

Mousa

Member
Location
Amman, Jordan
he would have to move the ct to the load side of cb a and b
leaving them on the 1 to a/b feeder would be an option, but not a good one
and still not protect the 1 to a/b feeder

so if the fault was beteeen 1 and a or b it would go undetected
he wants to protect the feed from 1 to a/b

CB A and CB B have there ZCT for gf protection, the issue about the CT which will trip CB1
All of this CTs to protect both sides (source and load breakers) from fg in the cable connection between them, the cables long around 150 m
 

Mousa

Member
Location
Amman, Jordan
that would not protect the 1 to a/b feeder which appears to be his intent

his question: can he parallel the 0 seq ct's to drive 1 relay to trip cb1?
yes
perfectly acceptable, std practice, as noted in the white paper


yes, the goal to protect CB1, CBs a and b already protected by there ZTCs and relays
thank you dear
 

Wyo721

Member
Location
Wyoming
CT's typically are not sequenced

CT's typically are not sequenced

What is the CT ratio? The burden on the relay? if one trips it takes out the entire system correct? What is the trip setting range on the relay? Which breaker does it trip? Lots of thoughts but mostly just questions? Who specs the equipment and designed the system?
 