Then are you allowed to apply a tripping circuit to it?CB1 (source breaker) is existing facility and out of our project scope!
Then are you allowed to apply a tripping circuit to it?CB1 (source breaker) is existing facility and out of our project scope!
And allow the other supply to keep on supplying.Mousa...
Second relay will aid in quickly determining which of the two circuits is faulted!
Regards, Phil Corso
And allow the other supply to keep on supplying.
Yes, obviously they would have to fitted on the load side of a and b.he would have to move the ct to the load side of cb a and b
leaving them on the 1 to a/b feeder would be an option, but not a good one
and still not protect the 1 to a/b feeder
so if the fault was beteeen 1 and a or b it would go undetected
he wants to protect the feed from 1 to a/b
Yes, obviously they would have to fitted on the load side of a and b.
But, in my opinion, that would be a better option. Especially if they are not yet installed.
Do you have such a thing as fault free zones?that would not protect the 1 to a/b feeder which appears to be his intent
Do you have such a thing as fault free zones?
Agreed. Do you how far CBa and CBb are from CB1?but it is good practice to cover long feeders
and keep the length between ct and cb as short as practical
imo use 2 relays or another ct (summed 1 per phase)
Then are you allowed to apply a tripping circuit to it?
he would have to move the ct to the load side of cb a and b
leaving them on the 1 to a/b feeder would be an option, but not a good one
and still not protect the 1 to a/b feeder
so if the fault was beteeen 1 and a or b it would go undetected
he wants to protect the feed from 1 to a/b
that would not protect the 1 to a/b feeder which appears to be his intent
his question: can he parallel the 0 seq ct's to drive 1 relay to trip cb1?
yes
perfectly acceptable, std practice, as noted in the white paper