Does anyone know what kind of connection (type, size, and quantity of wire) is typically required between an ATS and an elevator controller. This connection is to notify the controller that power is going to be transferred from normal to emergency and allows time for the cabs to drop to the main floor prior to power being "restored."

I can't seem to find any details on the actual connection anywhere!

Thanks,
Keri :D:D
 
I would run 3 #12s 3 #14s thhn/ thwn-2 or whatever I had on the job.

2 would be functioning, 1 as a spare.

Its just a set of dry normally open or normally closed dry contacts. Elevator is just looking for a contact closure or contact opening.

Make sure your transfer switch has this function. On some it is an option.

I have also had to put a set of contacts in the elevator disconnect switch to indicate to the elevator controller that power has been disconnected.

Joe Villani
 
yes, you basically get dry contacts.

if the power goes out, you won't get any advance warning to give the elevator. However, you could hold the transfer switch in the normal position, and send a signal to the elevator, and then switch to generator after a time delay.

YOu can also get transfer switches with a pre and post transfer contact. If someone presses the "test" button, the contact will close, and the ATS will wait a certain time before it transfers to generator.

"In phase monitoring" is also good to have with an elevator. If you transfer from one live source to another live source (both the utiltiy and generator have power), and if the two sources aren't in phase, it can be really bad on the motor.
 
Elevator Pre-Signal Feature

Elevator Pre-Signal Feature

Does anyone know what kind of connection (type, size, and quantity of wire) is typically required between an ATS and an elevator controller. This connection is to notify the controller that power is going to be transferred from normal to emergency and allows time for the cabs to drop to the main floor prior to power being "restored."

I can't seem to find any details on the actual connection anywhere!

Thanks,
Keri :D:D

All of these replies are giving you the correct info but allow me to elaborate on the subject.
Basically, an elevator pre-signal, pre-transfer feature signals the elevator controller prior to a hot-bus hot-bus transfer (both sources energized.) This normally occurs when the ATS transfers back from gen to utility during a power outage or as stated, when the test button is used for initiating the transfer. During a power outage the feature is not activated on transfer to gen since this is a dead-bus hot-bus transfer (no utility power on ATS.) This feature, although can be found on the older relay logic ATSs, was not normally required with the controllers that used relay logic. However, it is extremely critical with the newer solid state controller logic on new installs or when old equipment is upgraded. The point is that the car cannot be moving during the switching of the motor load from one hot source to another with solid state controllers. Equipment damage such as blown circuit boards and components in the elevator controller can and will occur.
Part of my business involves designing and installing this feature on older systems (25 to 35 yrs) that have been upgraded.
Normally what I find is that the elevator vendor requires 2 seperate dry contacts that either NO or NC depending on the particular design/ Manuf. One contact operates 20 sec (adjustable) prior to transfer of the ATS. This signal sends the car to the nearest floor and the doors open. After transfer occurs, the contact resets and the car continues as normal. The second set of dry contacts operates after the ATS is in the emer position. Usually this signal puts the controller in emer mode and only allows for 1 car to operate on gen since they are not designed to power the whole bank of cars. We call
this the Switch Position contact. When norm power is restored, the sequence repeats in the retransfer to utility and both
contacts reset for normal elevator operation.
So depending on how the spec is written I usually see (4) #12 or #14 gauge (THHN, 600V building wire) field wires pulled between ATS and elevator room. I always recommend pulling spare wires for future use: wire is cheap compared to labor ;)

PS: forgot to mention, on the older ATSs these field wires connect to a TB block and use plugin timers/relays. On the newer ATSs with microprocessors the connections are at the back of the processor and time delay is programmed in from the HMI touch pad.
 