I'm an inspector dealing with a pool designer that specifies a #6 copper bonding grid on a commercial pool project. I'm certainly on board with bonding the rebar of the pool, deck reinforcing, pumps, metallic pieces, lights, and other required pieces.
However, they're specifying that the #6 wire terminate at the panel's ground bar. :-?
My 2002 NEC specifically states "This section (680.26) does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode."
I see no reason to run the wire to the panel, as we're not grounding...We're bonding. The intent is not to try to clear a fault, it is simply to eliminate gradient differences between potentially energized parts and pieces. Seems to me that the designer is missing the point.
My question is this:
Should I allow it or prohibit it? Although I see no specific hazard in connecting to the panel, I see less hazard (or potential for hazard) in not doing it at all.
I appreciate everyones' opinion.
I'm an inspector dealing with a pool designer that specifies a #6 copper bonding grid on a commercial pool project. I'm certainly on board with bonding the rebar of the pool, deck reinforcing, pumps, metallic pieces, lights, and other required pieces.
However, they're specifying that the #6 wire terminate at the panel's ground bar. :-?
My 2002 NEC specifically states "This section (680.26) does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode."
I see no reason to run the wire to the panel, as we're not grounding...We're bonding. The intent is not to try to clear a fault, it is simply to eliminate gradient differences between potentially energized parts and pieces. Seems to me that the designer is missing the point.
My question is this:
Should I allow it or prohibit it? Although I see no specific hazard in connecting to the panel, I see less hazard (or potential for hazard) in not doing it at all.
I appreciate everyones' opinion.