Agree... but for NEC lingo on this subject, it is not a "connection".A splice is a specific type of connection.
Agree... but for NEC lingo on this subject, it is not a "connection".A splice is a specific type of connection.
Yes it is, I agree but the gec conductor is not complete. I do not see those as taps unless the GEC is complete. Take the two, so called, tap conductors and tap them at the end of the gec conductor--- is that not a splice.But the continuous requirement is for GEC conductors, not GEC tap conductors.
End of 250.64(D)(1)...
Taps are only permitted when you have multiple service disconnects that require a connection to the grounding electrode system....
What you are saying means I could take a #4 copper wire for a 200 amp service and run it 5' off the main electrode. Then I could "TAP" a conductor in the middle of the 5' piece and run it to the panel. That is a splice. No difference then what you are saying.
in this thread, the conductor is not a GEC, but a bonding conductor to the interior metal water piping system as required by 250.104
Why did he not give enough info? 200amp service. By 250.66 A it could have been #6cu or #4al
I realize that but I was trying to make a point. I guess I disagree with you, and others, whether the connection in the graphic is a tap. I just don't see this as a tap. IMO, you need to have something to tap from. The wire from the electrode connected to nothing is not a gec so how can you tap it.Taps are only permitted when you have multiple service disconnects that require a connection to the grounding electrode system.
Grounding Electrode Conductor. A conductor used to connect the system grounded conductor or the equipment to a grounding electrode or to a point on the grounding electrode system.
Dennis,I realize that but I was trying to make a point. I guess I disagree with you, and others, whether the connection in the graphic is a tap. I just don't see this as a tap. IMO, you need to have something to tap from. The wire from the electrode connected to nothing is not a gec so how can you tap it.
It looks to me that the code requires either the method shown in the graphic you posted, or individual GECs from the grounding electrode to the service disconnects. It appears to prohibit a single unspliced GEC running to one of the service disconnects with taps to the others. There would be no technical reason to support that, but it appears that is what the words require.(1) Grounding Electrode Conductor Taps. Where the service is installed as permitted by 230.40, Exception No. 2, a common grounding electrode conductor and grounding electrode conductor taps shall be installed. The common grounding electrode conductor shall be sized in accordance with 250.66, based on the sum of the circular mil area of the largest ungrounded service-entrance conductor(s). Where the service-entrance conductors connect directly to a service drop or service lateral, the common grounding electrode conductor shall be sized in accordance with Table 250.66, Note 1. A tap conductor shall extend to the inside of each service disconnecting means enclosure. The grounding electrode conductor taps shall be sized in accordance with 250.66 for the largest conductor serving the individual enclosure. The tap conductors shall be connected to the common grounding electrode conductor by exothermic welding or with connectors listed as grounding and bonding equipment in such a manner that the common grounding electrode conductor remains without a splice or joint.