I recently inspected a SFR for a rough wiring which was not complete because the location of the POCO UG feed was moved from the front of the house to the back. It has not been trenched yet and the service entrance equipment has not been installed.
The original, approved drawings showed the service entrance at the front left of the home which is the garage. There was suppose to be one 200A panel there.
When I got there, I found there were two 200amp panels that were fed with SE cable from the back of the house and the two panels were on the left side of the garage towards the back instead of where they were planned. Nothing is connected at the SE side and the SE cable is just curled up the the back left corner of the house (inside) that room will be a bedroom so I am assuming they will be installed an exterior disconnect. Who knows......
Anyway, they had already preplanned a Concrete Encased Electrode at the front left of the house (front wall of the garage) and there was plenty of slack in the #4 stranded bare copper to make it up the the originally planned panel.
Now they will either have to install the typical 2 ground rods at the rear exterior unless they run a grounding electrode conductor to the stub out of the CEE.
With that being said, anything short of an exothermic weld, would they not be required to make the connection using an aluminum or copper busbar to comply with 250.64(C)?
What is your opinion?
Besides the other issues of course that are causing me to return and ask for more information. I can only make another assumption that they are going to install a 320a continuous meter base for this application.
Thoughts?
The original, approved drawings showed the service entrance at the front left of the home which is the garage. There was suppose to be one 200A panel there.
When I got there, I found there were two 200amp panels that were fed with SE cable from the back of the house and the two panels were on the left side of the garage towards the back instead of where they were planned. Nothing is connected at the SE side and the SE cable is just curled up the the back left corner of the house (inside) that room will be a bedroom so I am assuming they will be installed an exterior disconnect. Who knows......
Anyway, they had already preplanned a Concrete Encased Electrode at the front left of the house (front wall of the garage) and there was plenty of slack in the #4 stranded bare copper to make it up the the originally planned panel.
Now they will either have to install the typical 2 ground rods at the rear exterior unless they run a grounding electrode conductor to the stub out of the CEE.
With that being said, anything short of an exothermic weld, would they not be required to make the connection using an aluminum or copper busbar to comply with 250.64(C)?
What is your opinion?
Besides the other issues of course that are causing me to return and ask for more information. I can only make another assumption that they are going to install a 320a continuous meter base for this application.
Thoughts?