I think what kwired said earlier in the thread about there not being a low enough resistance in the path back to the source was likely accurate- even with the downed line touching/very near all of that metal that was in good contact with the soil, just too much impedance.
And even though it has been pointed out about the voltage difference in video versus topic posting and iwire has said it was a mistake , I think it's still a good thread and still gives food for thought for the "earth" crowd- if soil as a fault clearing often doesn't work for higher voltages ( it for sure didn't work for the high voltage in the video), why would they believe it would be effective for the simple lower voltages used everywhere else?
You got me laughing on that one. Spot on.
Next time some guy says the earth is going to clear a fault on his 1/4 hp drill, show him that video.