Do wire connectors such as wire nuts need to be listed for wet conditions if used outdoors but in a weatherproof panel?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Inside a panel is not considered a wet location although I have seen some that were pretty wet..lol

If the inside of a panel was a wet location then your overcurrent protective device would have to be listed for wet location....
 