Every VFD must have what is called a "pre-charge circuit". The DC bus capacitors charge themselves instantly and will pull current at a rate commensurate with the AVAILABLE FAULT CURRENT at the rectifier terminals if allowed to. That rate of rise of the cpacitor charging current can damage the rectifier components and the caps themselves, even the transistors down stream. So to prevent that from happening, the pre-charge circuit uses some sort of method of limiting that capacitor charging current for the first few cycles whenever a VFD is powered up. most of the time, this is a current limiting resistor in series with the DC bus, then once the caps are charged, that resistor is removed from the circuit with a shunting contact (relay or contactor depending on size). In really small VFDs, this is sometimes done with an NTC (Negative Temperature Coefficient) thermistor, a type of resistor that has a high resistance when cold and the resistance drops as temperature rises. So it limits current for a second, then is almost non-existent (saves from having to add the relay). In some mid-size drives (which varies by mfr) the rectifier uses SCRs instead of diodes so the SCRs are ramped into full conduction which limits the current just like a soft starter, but that means adding a ramp control and firing board and SCRs are more expensive than diodes. So economically, they go back to resistors at some point.
If your VFD uses the resistor or thermistor method, those components have a finite life, usually around 2,000 operations. If you only power a drive up and down for maintenance or utility line loss situations, you never get to 2k operations in a normal lifetime of a VFD. But if you power up and down once per shift, 2 shifts per day, you get to 2k in less than 3 years. Once the pre-charge resistor burns out, the drive doesn't power up or if the relay/contactor welds, the rest of the components fail very quickly.
If your VFD uses the SCR method, you may never see a problem. The tricky part is going to be getting Yaskawa to tell you what they use on YOUR specific VFD, 125HP is right in the bread basket where some mfrs use that. But if they won't tell you, sometimes you can tell by looking at a recommended spare parts list. If it lists an SCR or rectifier firing board as a component, that means is isn't using a resistor.