hhsting
- Glen bunie, md, us
- Junior plan reviewer
Attached sketch shows two sets of service laterals (underground) from one electric utility transformer going to each service disconnects.
Both service disconnects are grouped at the building exterior. The building has one tenant only.
One service lateral is 4#250kcmil Al and second is 4#4/0 awg Al. Service point is at the service disconnect line side terminal
I am not sure if I am allowed to have two sets of service lateral or not. Its confusing
Would NEC 2014 section 230.2 first paragraph apply here or not? Is the attached sketch considered one service or two services?:
“For the purpose of 230.40 exception no. 2 only underground sets of conductors, 1/0awg and larger, running to the same location and connected together at their supply end but not connected together at their load end shall be considered to be supplying one service”
230.40 exception no.2:
“Where two to six service disconnecting means in separate enclosure are grouped at one location and supply separate loads from one service drop, set of overhead service conductors, sets of underground service conductors, or service lateral, one set of service entrance conductors shall be permitted to supply each or several such equipment enclosures