Alright so this is how it is forget post #1.
I have shopping center. Space is empty so they are splitting it to two tenants. Please see attached sketch label shopping center below. Hash tag lines is tenant space to be modified:
The space to be modified is going to have 1 hour rated fire wall splitting one tenant space now to two. Please see attached sketch the space blown up with 1 hour rated wall creating tenant Space 1 and tenant Space 2
Now the space has main service disconnect of tenant #1 and main service disconnect of space #2 on the backside wall of tenant space #1 as shown below with meters for both tenants next to them. The trough is also their but didn’t have room to show it
The way its wired from one POCO xfmr dedicated to severing only space#1 and #2 has two separate service conductors (not sure service lateral or service entrance) go underground to tenant space 1 come up trough backside wall of tenant space 1, go into trough and then to each respective meter and to respective each tenant service disconnects. Please see elevation view exactly how
Please see below Equipment location and Elevation:
The way plans show grounding bonding is one grounding electrode tap from each service disconnect go to common ground electrode conductor of wire type which then has bonding jumper to steel, water pipe, rod, and to inter system bonding termination(1 for both tenants??). Its following 250.64(D). Not 250.64(F). Its specifiaclly only following NEC 2014 section 250.64(D)(1). The Common grounding electrode is wire type sized 2/0 awg copper. Please see below configuration
So now you have all the picture.
Questions then are:
1. Is this one service or two services per NEC 2014 section 230.2?
2. Would NEC 2014 section 250.64(D) or 250.64(F) apply?
3. Tenant space #2 main service disconnect is at the back wall of tenant space #1 with tenant space #1 service disco. Would this be NEC 2014 not compliance with any code?