richwaskowitz:
Assuming you really have to live with these somewhat centralized power sources, then can you use an Edison distribution system? In other words three wires.
With an Edison system you only have voltage drop on one wire. Also feed the loads from the center.
I will use some simple values. Per wire maximum current is 7.5 A (1/2 of the power supply because of center feeding). Approximate wire resistance of #14 copper at 2.5 ohms per 1000 ft, or 0.07 ohms per 25 ft by rounding up. This somewhat compensates for wire temperature rise.
Assume 1 A per ArmorStart. Put one ArmorStart at the power supply. Thus, we only start with 7 A to the distribution line.
At 1st 25 ft location from power supply the voltage is Vps - 0.49, the drop to the next is 0.42, and as follows 0.35, 0.28, 0.21, 0.14, 0.07 and we are done. Total drop is 1.96 V, or using 24 V as the source, then 24 - 2 = 22 V at the last ArmorStart. Use your own figures.
If we assume that the only time that power is switched on to ArmorStarts is when the 24 V power supply is powered, then you can probably ignore any initial inrush current. Thus, the real important current to know is the peak current used when the ArmorStarts are working and doing their intended job.
.