I think there?s something wrong with my departments enforcement of 250.50 that has been enforced from long before I came here and I?d like some opinions. . If I see a service on a building will no electrodes present, there needs to be an electrode installed, usually a ground rod. . If the service is on a pedestal, we consider it a structure served and need to see the ground rod at the pedestal. . The building supplied by the pedestal or a second building supplied from the first building can be supplied as a subpanel, with separated neutral and ground [250.32(B)(1)] or supplied like a main, with combined neutral and ground [250.32(B)(2)], but either way each structure must have its own electrode.
Now here?s where I see the inconsistency.
For a generator not in the building it powers, located either outside or in its own ?doghouse? that?s a separate structure from the building that it powers.
If a generator transfer switch breaks and transfers the grounded [neutral] along with the phase conductors, the generator is separately derived, has combined neutral and ground on the generator and, as a separate structure, has to have its own ground rod [electrode]. . But if the generator transfer switch does not break and transfer the neutral, the generator is not separately derived, needs to have separated neutral and ground but does not have to have its own ground rod.
When I ask why we don?t enforce a ground rod for a ?subpanel? generator, the answer I get is that it?s not separately derived. . When I ask how a ?subpanel? generator is different from a second building subpanel feed [250.32(B)(1)], I don?t get an explanation.
What do you think ?
David
Now here?s where I see the inconsistency.
For a generator not in the building it powers, located either outside or in its own ?doghouse? that?s a separate structure from the building that it powers.
If a generator transfer switch breaks and transfers the grounded [neutral] along with the phase conductors, the generator is separately derived, has combined neutral and ground on the generator and, as a separate structure, has to have its own ground rod [electrode]. . But if the generator transfer switch does not break and transfer the neutral, the generator is not separately derived, needs to have separated neutral and ground but does not have to have its own ground rod.
When I ask why we don?t enforce a ground rod for a ?subpanel? generator, the answer I get is that it?s not separately derived. . When I ask how a ?subpanel? generator is different from a second building subpanel feed [250.32(B)(1)], I don?t get an explanation.
What do you think ?
David