Consistent enforcement of 250.50

Status
Not open for further replies.
David, In general, We install ground rods at structures that have foundations built.(Generator pads light bases, cooling towers for hvac etc). The exception to article 250.32 allows us not to use a rod at condensing units, and if it's on a surface mount pad i would'nt think it was built.

Exception: A grounding electrode shall not be required where only a single branch circuit supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the conductive non?current-carrying parts of equipment. For the purpose of this section, a multiwire branch circuit shall be considered as a single branch circuit.
Rick
 
RUWired said:
Exception: A grounding electrode shall not be required where only a single branch circuit supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the conductive non?current-carrying parts of equipment. For the purpose of this section, a multiwire branch circuit shall be considered as a single branch circuit.
Rick

That exception will work for the AC Condenser but how many pool equipment pedestals have only a single or multiwire branch circuit ?
 
Since I had never read 250.30(A) before with the Article 100 definition of the word "structure" in mind, I had never considered the possibilities. . I just can't imagine telling a ELC pool installor that he needs to either
run his service plug curcuit to a separate pedestal and blank off the service plug opening in the pool equipment cabinet
or
install a ground rod at the pool pedestal.

Is there anybody anywhere that is enforcing 250.30(A) for pool pedestals ?

David
 
georgestolz said:
At the risk of exposing my ignorance, what exactly is a pool pedestal and what does 250.30(A) have to do with it? Was that a typo for 250.32(A)?

Second, was my question about 250.30(A)(7) that far off base, that it didn't even warrant an acknowledgement?

Yes 250.30(A) was a typo
It's 250.32(A)

250.32(A) & 250.30(A)(7)x1 both require an electrode for a seperately derived system. . 250.32(A) is more specific, talking about a separate building or structure. . So it's requiring separate electrodes for separate buildings even if they're part of the same separately derived system.

I'm assuming that the reason that you prefer 250.30(A)(7) is that it specifies the electrode to be "as near as practicable" the connection of the conductor to the main. . If you supply the second building according to 250.32(B)(1), you have one electrode serving both buildings with a connection at the main to a single equipment grounding system that has feeders and homeruns thruout both buildings.

I don't see 250.30(A)(7) as requiring a separate electrode at the second building.

Once you encounter a transformer, either with the one building, or supplying a second building, then you have another separately derived system and 250.30(A)(7) requires a separate electrode for that additional system.

The problem that I see with using 250.30(A)(7)x1 is that it doesn't differentiate between sections of one single separately derived system. . Since the same utility transformer that supplies the residential house service also powers the feeder to the second building / garage, 250.30(A)(7) doesn't require a separate electrode for the second building. . It only requires one electrode per separately derived system [with the exception of the supplementing requirement of 250.53(D)(2)]. . The house and the detached garage are in the same separately derived system. . One rod at the house satisfys 250.30(A)(7).

250.32(A) requires an additional rod at the garage [or other second building]. . And as we're debating, it requires an additional rod at additional "structures" that don't fall under the exception.

A pool pedestal is a free standing support for pool equipment. . According to the NEC definitions, it's also a "structure". . It could be a 4x4 post or posts or metal post(s) with or without cross pieces and backboards for mounting equipment.

They are very common in northern Ohio and usually have a service plug built right into the enclosure with all of the other pool electrical. . I've never seen this all-in-one type supplied with fewer than 3 circuits and usually has a 240volt 2pole breaker included. . It doesn't fall under 250.32(A)x which only eliminates the electrode requirement for one circuit and multiwire circuits.

David
 
Last edited:
Anybody care to write a code proposal that would change the Article 100 definition of "structure" into a definition that is useful ?
 
Got a starting point? I've tried once, it was a bit of a bugger to define using different words.

Thanks for bumping this thread, I want to look at it this evening - I'd forgotten about it. :)
 