There was an "incident of concern" at work last week. The local POCO (my relatively recent daytime employer) energized a homeowner installed, underground fed, 120/240v construction temporary. A couple of hours later, the customer calls and says that there's something wrong with "our" power. A serviceman is dispatched, opens up the temp and finds a few "modifications".....One of the #4's from the load side of the meter socket to the little 4 ckt mlo had been removed and replaced with a #6 white thhn and now went from meter lug to NEUTRAL buss! The main bonding jumper had been removed and another piece of white #6 had been jumpered across the lugs of the mlo. This was inspected and "green tagged" by the local AHJ.