megloff11x
Senior Member
A company that will remain anonymous substituted a discontinued contactor with their latest and greatest. The new model has inrush current that reminds me of that Japanese guy who wolfs down the hot dogs. I have four of them that draw a little over an amp total between them in steady state, but close to 30A when the button is pushed. The typical button set up in a start/stop loop has 10A contacts. I don't care if the ratings are based on steady state. I see welding in the future if I don't pilot this set up with another relay with a less demanding coil, but fat enough contacts to handle the 83ms duration surge.
I noticed the problem when the system tripped an overload protection circuit in the DC power supply providing the 24V. It never happened with the older model contactors. I had to get a bigger DC supply too.
Has anyone else had this issue, and how much ampacity did you make your pilot relay's contacts?
Matt
I noticed the problem when the system tripped an overload protection circuit in the DC power supply providing the 24V. It never happened with the older model contactors. I had to get a bigger DC supply too.
Has anyone else had this issue, and how much ampacity did you make your pilot relay's contacts?
Matt