Makes sense. I'll know more when I get to actually check it further.The motor could read bad but would be a symptom, not a problem. If the motor had a open or short, the controller would open the circuit, but not burn up. However if the controller caused a prolonged single phasing situation, it could fry the motor. Like if two sets of contacts welded together in the controller, it tried to open the circuit on overload, but only the third set of contacts actually opened, it would cause the motor to single phase.