on a 120volt definite purpose contactor does just the 120 volt power terminate to the contactor and energize the power or does the hot and the neutral terminate at the coil?
If the control power is referenced to the neutral, yes. There will be two coil terminals and you can supply the needed voltage to them any way you want (within reason.)so on a 120volt definite purpose contactor the control power and the neutral both terminate on the contactor?
the control power has its own neutral to hold coil once control circuit is energized. the circuit your "contacting" running through does not require neutral at contactor. just like a switch. contactor is a switch controled remotely or automatically via whatever the control or coil circuit being controlled byso on a 120volt definite purpose contactor the control power and the neutral both terminate on the contactor?