zbang
Senior Member
- Location
- Roughly 5346 miles from Earls Court
Ah, I see what's going on.... in delta 1M and 2M are closed and thus sharing current. In wye, it's 1M and 1S where 1M carries full current but it's wye current so lower.
Hmm, I think I'm starting to understand. So the current flows through two contactors allowing a lower rating than the motor?In a Y-D starter, the two main contactors are sized fir a minimum of 58% of the motor FLC, the Shorting contactor is sized at 33%. The OL relay is likewise set for 58% (unless it is ahead of the entire starter).
The HP ratings on the labels of the individual contactors become meaningless in this case. Whomever the OP spoke to at ABB and the vendor is clueless. This is why I hate dealing with Y-D starters. I used to build them from scratch, but 90% of the people who use them in the field do not fully understand them. I’ve seen more catastrophic mistakes made with Y-D starters than any other technology, right up to the point of motor destruction.
The contacts may fail or weld closed if they are not sized to the motor starting current.Could you expand on that? I don't think I understand contactors well enough. Is it basically the power required to make the connection and break the connection? So if you undersize it, it may have issues starting and stopping?
Those are the usual sizes most suppliers provide to customers of wye-delta starters.Hmm, I think I'm starting to understand. So the current flows through two contactors allowing a lower rating than the motor?
Hmm, I think I'm starting to understand. So the current flows through two contactors allowing a lower rating than the motor?
125% ... of what?... Motor conductors ALWAYS need to be sized to 125% ...
Of the running full load, just like any other conductor supplying a continuous load does.125% ... of what?
When you're starting from a dead stop, in Y configuration, your nominally 480-volt, 200 Hp motor is actually an 830-volt, (480√3) 67 Hp motor.
When making the transition from Y to Δ, it's already spinning. The transition pickup current is significantly less than the current of an across-the-line start from a standstill in Δ configuration.
If you don't have a rigorous understanding of this, it would be best to abandon the Y-Δ approach and use a soft starter or VFD.
On the other hand, If you do have a rigorous understanding, it would be best to abandon the Y-Δ approach and use a soft starter or VFD.
Not only that!125% ... of what?
When you're starting from a dead stop, in Y configuration, your nominally 480-volt, 200 Hp motor is actually an 830-volt, (480√3) 67 Hp motor.
When making the transition from Y to Δ, it's already spinning. The transition pickup current is significantly less than the current of an across-the-line start from a standstill in Δ configuration.
If you don't have a rigorous understanding of this, it would be best to abandon the Y-Δ approach and use a soft starter or VFD.
On the other hand, If you do have a rigorous understanding, it would be best to abandon the Y-Δ approach and use a soft starter or VFD.
Not only that!
If you fail to consider the infinitesimal transition period from the wye-mode to the delta-mode, your contactor contacts can get damaged due to a possible "short-circuit" when the parting contacts of the wye contactor still have an arcing connection and the delta-mode contacts make!
[125%] Of the running full load, just like any other conductor supplying a continuous load does. ...
Which is fine but the 125% applies to conductors, selecting appropriate contactors is sort of a different game.Yes, yet another reason to relegate the Y-Δ approach to the dustbin of history. A well-integrated, well thought out controller would have considered all that, and included delays & sequencing to assure that it doesn't happen. But if I recall correctly, the original post was asking for assistance cobbling something together from a basket of loose parts.
Yes, for the conductors feeding it, for complying with code. But if I recall correctly, the original post expressed concerns about the contactors being too small for the current they'd be carrying.
Yes, not easy.I agree with those who say that this type of starting scheme should be sent to the museum. With modern methods using them is rare. The only time in my career that I've seen this is when an engineer specified this type of starter for a fire pump. Another problem that I see is that finding an electrician who actually can correctly wire these is not easy.
Only once for the W-D.I've encountered part winding and auto transformer starting methods but never actually seen wye-delta in the wild.
My experience is that wye-delta is a very common starting method through Europe and maybe the rest of the world except North America. It seems every IEC contactor manufacturer has premade busbars and interlocks in their catalogs.I agree with those who say that this type of starting scheme should be sent to the museum. With modern methods using them is rare. The only time in my career that I've seen this is when an engineer specified this type of starter for a fire pump. Another problem that I see is that finding an electrician who actually can correctly wire these is not easy.
I think maybe partly because their motors are more likely to be wound with necessary leads made available to do so. They also seem to mostly have delta wound motors where it seems there is a lot of wye wound motors in North America, with no ready access to the wye point. Even delta wound motors often don't have access to every individual winding end lead, just enough to make them dual voltage capable most the time. Though under ~100 HP not many are using reduced voltage starting for utility impact reasons but do use electronic soft starters or VFD's in those lower HP motors for mechanical shock reasons.My experience is that wye-delta is a very common starting method through Europe and maybe the rest of the world except North America. It seems every IEC contactor manufacturer has premade busbars and interlocks in their catalogs.
But in 40 years, I don't think I was ever involved in much more than 20 installations of them.
I've encountered part winding and auto transformer starting methods but never actually seen wye-delta in the wild.