Pushing in contacts not 100% full proof. Sometimes contactors & starters movement gets sluggish and even with full power ( coil voltage ) will not pull in all contacts. We had over a hundred Danfoss VFD'S that were exercised every month during ATS testing. Had to replace at least 8 GE junk M2 contactors every year that while receiving 118 to 121 volts to coil would not fully seal contacts. So prefer to perform testing with power on. Usually quicker. When a three phase motor is single phasing from lost of one phase and power travels thru a contactor & a starter will remove motor leads from last set of contacts then take voltage readings. I'm old school and prefer to use a Ideal Voltron tester because it places more load on the circuit. With a digital meter especially in a damp location and while only having one lead on a 480 volt source and other test lead in the air often will get 50 to 90 volt reading. Started out using a Simpson model 260 analog meter and old reliable Square D "Wiggee " tester. Found the Wiggees to work great troubleshooting lost of power on circuits.