Re: Contactors
All contacts actually have three different ratings: Make, Break and Continuous.
"Make" is the amount of current the contacts can handle when they turn something on. Most people know inductive loads, like motors, can have inrush currents of 6-10 times full load amps, but negative temperature co-efficient loads, like halogen lamps can have even higher inrush currents.
"Continuous" is the normal constant current that can be carried. It makes no difference what the load is, amps is amps.
"Break" is the amount of current a contact can turn off. This is probably the most commonly misapplied switch rating because it is often only a fraction of the other two ratings. Horsepower rated devices are rated to break the same amount of current as they can make, this is why their HP rating may be so much lower than their continuous current rating.