Re: Contactors
Folks the voltage being applied to alll 4 contactors is 119 VAC total amperage pull when t101 comes on is 4.2 amps total. I have tried them all by themselves I have tried them in groups of 4 and groups of 2 all to no avail. The power circuit for the timer is on its own dedicated circuit, actual wiring length is 18 inchs box is metal not pvc got ( 2 locations mixed up)
Well went to Grainger got a dedicated contactor 120 volt coil 4 pole 30 amp resistive load each pole.Brought it back to the job site. The original contactors were steel based so I figured what the heck I mounted it outside the box on a piece of plywood and it worked but if cycled 3 4 times it failed also.
So anyway I installed the least of brand x contactors on a piece of wood in the box no noise?
Then I installed the square d contactor and it worked 12 times in a row no noise no nothing just great operation.
Tomorow I throw out the brand Xs and install the square d 4 pole insulated contactor, that I ordered at Graingers.
Near as I can figure the ces man contactors have a very high failure rate, I called other ces and they verified that 6-8 out of 10 fail within 5 minutes or they are okay indefinitely.
Folks the voltage being applied to alll 4 contactors is 119 VAC total amperage pull when t101 comes on is 4.2 amps total. I have tried them all by themselves I have tried them in groups of 4 and groups of 2 all to no avail. The power circuit for the timer is on its own dedicated circuit, actual wiring length is 18 inchs box is metal not pvc got ( 2 locations mixed up)
Well went to Grainger got a dedicated contactor 120 volt coil 4 pole 30 amp resistive load each pole.Brought it back to the job site. The original contactors were steel based so I figured what the heck I mounted it outside the box on a piece of plywood and it worked but if cycled 3 4 times it failed also.
So anyway I installed the least of brand x contactors on a piece of wood in the box no noise?
Then I installed the square d contactor and it worked 12 times in a row no noise no nothing just great operation.
Tomorow I throw out the brand Xs and install the square d 4 pole insulated contactor, that I ordered at Graingers.
Near as I can figure the ces man contactors have a very high failure rate, I called other ces and they verified that 6-8 out of 10 fail within 5 minutes or they are okay indefinitely.