From another thread: http://forums.mikeholt.com/showthread.php?t=102972
1) I will be changing over from #2 AL SER, 2-2-2-4, to #2 AL XHHW in the crawl space. I’m using 1-1/4” PVC. According to 314.28(A)(2) 6 x 1-1/4”= 7.5” so I would need a box at least 8”, correct?
2) Table 250.122
80 amps would need a #8 CU. Would you pull the #8 CU or would you keep with the #4 AL?
Thanks as always.
1) I will be changing over from #2 AL SER, 2-2-2-4, to #2 AL XHHW in the crawl space. I’m using 1-1/4” PVC. According to 314.28(A)(2) 6 x 1-1/4”= 7.5” so I would need a box at least 8”, correct?
2) Table 250.122
80 amps would need a #8 CU. Would you pull the #8 CU or would you keep with the #4 AL?