I just had an inspection in a city I normally don't work in (service upgrade).
Everything was OK, however the inspector didn't like the way I did the EGC. I ran an EGC from the new panel to the 1" copper water main where it enters the foundation, and I ran another EGC from the new panel to an 8' ground rod near the new panel.
The problem she had with it, is that it was two pieces of wire (one for each system). She wanted one continueous wire from the rod to the pipe to the panel.
It's not really a big deal, but it seems to me that the way I did it is more fail safe. If I do it her way, there is really the single ground point (the pipes) which are grounded additionally by the rod. In my way they are two completely different systems. Even if the EGC to the pipes gets broken, the completely differnet rod system still grounds the system.
I thought the the requirement for continuous EGC referred to splices between the ground rod (or pipes) and the panel, not between the two systems.
Is she right? FYI she passed the job, this is just for future reference)
Thanks
Everything was OK, however the inspector didn't like the way I did the EGC. I ran an EGC from the new panel to the 1" copper water main where it enters the foundation, and I ran another EGC from the new panel to an 8' ground rod near the new panel.
The problem she had with it, is that it was two pieces of wire (one for each system). She wanted one continueous wire from the rod to the pipe to the panel.
It's not really a big deal, but it seems to me that the way I did it is more fail safe. If I do it her way, there is really the single ground point (the pipes) which are grounded additionally by the rod. In my way they are two completely different systems. Even if the EGC to the pipes gets broken, the completely differnet rod system still grounds the system.
I thought the the requirement for continuous EGC referred to splices between the ground rod (or pipes) and the panel, not between the two systems.
Is she right? FYI she passed the job, this is just for future reference)