Hello, long time reader first time poster. A little about myself, I have over 10 years manufacturing/facilities maintenance and automation experience where I was the plant electrician. I also have over 20 years of large food service equipment installation / maintenance / service and repair.
Here is my first question: I recently relocated a 45kva transformer from one location of my building to another. I removed all wires from both the 480 volt disconnect and from the 208 panel and left all connections inside of the transformer intact. All phase wires, neutral wire and ground wires were all color coded previously. The transformer was fed from the building's MDP and the transformer fed a 120/208 3phase panel that only had a few circuits coming out of it. There is another 120/208 panel right next to this one that is fed from a 150kva transformer. I relocated the few circuits to the 2nd panel and then that is when I removed the 45kva transformer. After relocating the transformer to it's new permanent location, I ran the 480 volt wires from the same breaker that was used before but in a different location in the MDP. I then connected the secondary wires to a different 120/208 3 phase panel (I did not relocate the old panel). I removed this 120/208 panel from our previous location and re-installed it in the new location with the 45kva transformer. Before I was about to turn the breaker on to supply power to the transformer I took my multi-meter and checked for continuity between phases, neutral and ground and the meter read continuity between all. All phase wires, the neutral wire and the ground wire inside of the 120/208 panel have continuity between them all. I checked for continuity between the phase wires coming off of the breaker in the 480 volt panel that feeds the transformer and they have continuity between them as well. I am obviously hesitant to power the transformer and potentially injure myself or the equipment.
Is this situation normal? Why would I have continuity between phase wires coming off of a breaker that was previously in working condition and to have continuity between all wires inside of the 120/208 panel? Like I mentioned earlier, the transformer is fed from the same 480 volt panel that it was previously the only difference is the 120/208 volt panel which was also working fine previously. Any insight would be greatly appreciated.
Here is my first question: I recently relocated a 45kva transformer from one location of my building to another. I removed all wires from both the 480 volt disconnect and from the 208 panel and left all connections inside of the transformer intact. All phase wires, neutral wire and ground wires were all color coded previously. The transformer was fed from the building's MDP and the transformer fed a 120/208 3phase panel that only had a few circuits coming out of it. There is another 120/208 panel right next to this one that is fed from a 150kva transformer. I relocated the few circuits to the 2nd panel and then that is when I removed the 45kva transformer. After relocating the transformer to it's new permanent location, I ran the 480 volt wires from the same breaker that was used before but in a different location in the MDP. I then connected the secondary wires to a different 120/208 3 phase panel (I did not relocate the old panel). I removed this 120/208 panel from our previous location and re-installed it in the new location with the 45kva transformer. Before I was about to turn the breaker on to supply power to the transformer I took my multi-meter and checked for continuity between phases, neutral and ground and the meter read continuity between all. All phase wires, the neutral wire and the ground wire inside of the 120/208 panel have continuity between them all. I checked for continuity between the phase wires coming off of the breaker in the 480 volt panel that feeds the transformer and they have continuity between them as well. I am obviously hesitant to power the transformer and potentially injure myself or the equipment.
Is this situation normal? Why would I have continuity between phase wires coming off of a breaker that was previously in working condition and to have continuity between all wires inside of the 120/208 panel? Like I mentioned earlier, the transformer is fed from the same 480 volt panel that it was previously the only difference is the 120/208 volt panel which was also working fine previously. Any insight would be greatly appreciated.