Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
Nec 200.2 says that a grounded conductor cannot rely on connection to a metal enclosure, raceeay or cable armor.
However nec does not list receptacles here.
We are then referred to 300.13B which does not allow neutral continuity for multiwire branch circuits.
This concept is easily understood because loosing a neutral in a MWBC will result in elevated voltages for loads and may cause equipment damage
However, i now question whether standard daisychain receptacles for a standard non multiwire branch circuit would be code compliant since a receptable being removed would interfere with the grounded conductor continuity downstream?
I do not think NEC is dissallowing this but i worked with someone who disagreed
I know this would not cause harm as it would in a MWBC
What i mean by daisychain is line to right side of receptacle and neutral to left side, instead of one continuous line and neutral with pigtails