NEC 2008 has a new section (200.2 B) that mentions "The continuity of a grounded conductor shall not depend on a connection to a metallic enclosure, raceway, or cable armor."
To be honest I'm not sure if I'm interpreting this correctly. I know in the past you could use metallic conduits and boxes as your connection to ground. For example, if you had a 120 V circuit in EMT, you could install a live wire, a neutral wire, and use the conduit and box as a ground connection.
Does this new section in NEC 2008 prohibit this practice? What exactly is the change here? The illustrations I see showing the change are not too clear. Any help would be appreciated. Thank you.