Re: Continuous current on an equipment ground conductor.
Charlie, everything you say makes sense. It is on questions like this that I wish I had a grant to pay for the rent in a warehouse where we could lay out conductors and actually measure some of these values, changing the conditions as we went along.
Brian, I am interested in this partly because I once measured an average of about 16A on each of 6 large EGCs which ran with 6 3-phase feeds to roof-top HVAC stuff. I was puzzled, and so I put my flexible ammeter probe (AMEX) around pairs and recorded results. This showed that they were at different phase angles which were not necessarily 120 deg apart. All I could conclude was that the current was induced from the 6 conduits they came from. (There was in addition current on building steel, plus some leakage N/G, so it was complicated).
I was not able to snake a probe around all of them, but wondered if it would read something close to zero.
Karl