Ed, ?A? is single point grounding. There would be some minute common mode current flow between the ground electrodes. But it would not cause any problems down stream from the N-G bond point, since the voltage developed would be at the same potential or reference. The key installation issue is to keep all the GEC?s grouped together side-by-side, and making the MBJ and EGC adjacent to one another.
?B? is another single point ground. This closely resembles the method used by all telephone companies, and is the recommended practice by ANSI, BICSI, Bellcore TIA/EIA, and others. Again small amounts of common mode current will flow between ground electrodes, but again as in ?A? the SPG eliminates any problems.
C&D are both code violations. ?D? is a multi-grounded-neutral, and significant current would flow in the GEC. ?C? looks a lot like a service entrance, but would not be allowed on premises wiring.
Again I would like to point out that true single point grounding is extremely rare, and not possible in most circumstances. To have truly SPG would require complete electrical isolation of all raceways and equipment downstream from the N-G bond point. There could be no incidental or intentional contact with any type of ground like cement, rebar, building steel, or any conductive surface. Very few industries even attempt to pull it off. Its reward is great if you can do it. It would be impossible for lightning current and common mode current to flow.