Not per 210.19(A)(1) alone. Any table value of 125A or greater would satisfy its requirement. Your OP conditions limited the determination to THHN Cu, so #2 rated at 130A would meet the requirement.
100 amp continuous load THHN copper conductors 6 CCC's in a raceway 75? terminations.
Determine the minimum size OCPD and conductors.
Step 1 Minimum size OCPD
210.20 Minimum size OCPD = continuous load x 125%
100 x 125% = 125 amps
240.6 Standard size OCPD
125 amp OCPD is a standard size so this is the minimum size OCPD
Step 2 Minimum size conductors
210.19 (A) (1) The minimum size branch circuit conductors, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125% of the continuous load.
100 x 125% = 125 amps.
Table 310.16
We can't use 90? column based on 110.14 (C) (1) (b)
So the smallest conductor would be a #1 THHN 310.16 75? #1 = 130 amps.
210.19 (A) (1) has been satisfied along with 110. 14 (C) (1) (b) and 240.4 (B)
Step 3 Adjust for more than 3 CCC?s in a raceway
110.14 (C) Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
In step 1 we determined that a #1 was the smallest size conductor allowed.
Now there are 6 CCC's in a raceway Table 310.15 (B) (2) (a) 4-6 conductors adjust conductor ampacity to 80% of Table 310.16 ampacity.
Table 310.16 #1 THHN @ 90? = 150 amps
150 x 80% = 120 amps
Step 4 Verify conductor is sized properly
#1 THHN with an adjusted ampacity of 120 amps
Can this conductor terminate on OCPD determined in step 1. YES
Does this conductor comply with the minimum size conductor determined in step 2. YES
Does the conductor have a final ampacity not less than the maximum load to be served. YES
Does the conductor comply with the rules in 110.14 (C) YES
Remember the definition of ampacity
Ampacity. The current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating.
This question was to find out what everyone thought about adjustment and correction factors for continuous loads. Do the conductors have to have an ampacity of 125% of the continuous load after corrections and adjustments? (This is the way I had been taught.)
Or, do they need to have an ampacity not less than the maximum load to be served after adjustments and corrections along with following the rules in 240.4 (B), 110.14 (C) (1), and 210.19 (A) (1)? (The way I believe now.)
Hope this clears things up
Clear as mud