I have what is simple question regarding branch circuit laods for a computer work station in an office.
I have four work stations in a single office. Each work station has a computer tower drawing 6 amps and a monitor drawing 2 amps. At 120 volts I see this as a 960va load. The work station will run continuosly so I believe I must have a 125% X 960 demand or 1200va. Is this correct? If so It appears I can not supply any two work stations with the same 120v/20amp circuit, is that correct?
Thanks for any input
I have four work stations in a single office. Each work station has a computer tower drawing 6 amps and a monitor drawing 2 amps. At 120 volts I see this as a 960va load. The work station will run continuosly so I believe I must have a 125% X 960 demand or 1200va. Is this correct? If so It appears I can not supply any two work stations with the same 120v/20amp circuit, is that correct?