Here's the situation: House has subpanel for its pair of storage-tank water-heaters. Wattages are 3500 and 4500, and they are protected by 20- and 30-amp breakers, respectively (at 240v); thus each easily complies with the 80% factor for continuous loads. Question: is it code-compliant to protect the subpanel feeder with a 40-amp breaker in the main panel ? Since 40-amps*240-vac is 9600 watts, and the sum of the water heater loads is 8000 watts, the 80% factor is missed.
I believe the applicable code is "“Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.” So the question becomes, is a subpanel feeder also considered a branch circuit (from the point of view of the main panel) ?
Assuming this is compliant, what about practical issues ? As far as safety, surely there's no overheating danger in protecting the feeder with a smaller breaker (40-amp instead of 50-amp). How likely are nuisance trips of the 40-amp breaker ? The 40-amp breaker provides a margin of 120% instead of 125%; that's pretty close Given a water-heater rarely runs continuously for 3 hours, never mind two doing it simultaneously, I wouldn't expect problems.
I believe the applicable code is "“Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.” So the question becomes, is a subpanel feeder also considered a branch circuit (from the point of view of the main panel) ?
Assuming this is compliant, what about practical issues ? As far as safety, surely there's no overheating danger in protecting the feeder with a smaller breaker (40-amp instead of 50-amp). How likely are nuisance trips of the 40-amp breaker ? The 40-amp breaker provides a margin of 120% instead of 125%; that's pretty close Given a water-heater rarely runs continuously for 3 hours, never mind two doing it simultaneously, I wouldn't expect problems.