physis
Senior Member
I do...I have seen a lot more open neutrals on the line side of the service than on the load side.
Really? I've only seen that like twice. I guess my experience is somewhat limited.
I do...I have seen a lot more open neutrals on the line side of the service than on the load side.
If I were to put stat's to it ~ it would be:Really? I've only seen that like twice. I guess my experience is somewhat limited.
Which - in one way, makes having a current carrying nipple between the meter and main - 'safer' - if the neutral fails between them the building has a better chance of not going Hi/Low. (So long as there is a relatively good connection on both sides.)
I'm curious about something here. Are we talking about straight out neutral loss or degradation of continuity? Not that it really matters I guess, but objectionable current usually comes from loss of integrity on the load side of the service and it seems like what's mostly being talked about here is total neutral loss on the power company side. But maybe I'm seeing this funny.
Yes, the conduit may carry half or even more of the grounded conductor current, but I don't see it as a hazard. If there is a poor connection, the resistance of the connection will limit the current and the only voltage available to drive the current is the voltage drop on the grounded conductor.Even with perfect neutral connections under normal operating conditions the conduit will pick up a large portion of the imbalanced neutral current. Of course if the neutral starts to degrade the current on the conduit will rise.
If there is a poor connection, the resistance of the connection will limit the current and the only voltage available to drive the current is the voltage drop on the grounded conductor.
Even if it were connected, it would still be carrying 50% of the current -
My post was based on a system with a grounded conductor that is in good condition. If there is a high resistance connection in the parallel path (conduit) more current will flow on the grounded conductor. The only voltage to drive the current through the poor conduit connection will be the voltage drop on the grounded conductor. The voltage drop across the poor conduit connection cannot exceed that of the grounded conductor itself. Of course if the neutral has a problem we can have both a shock and fire hazard at the conduit.It's more like this.
The current is limited by the resistance but the current across any conductive system is the same all the way across it.
A voltage drop exists across any and every resistance. This is where a shock or a fire hazard might exist.
If you multiply the current through the system by the voltage across a junction you get the wattage or power at that junction. That's where the fire hazard comes from.
The voltage across that same junction is where the shock hazard comes from.
My post was based on a system with a grounded conductor that is in good condition. If there is a high resistance connection in the parallel path (conduit) more current will flow on the grounded conductor. The only voltage to drive the current through the poor conduit connection will be the voltage drop on the grounded conductor. The voltage drop across the poor conduit connection cannot exceed that of the grounded conductor itself. Of course if the neutral has a problem we can have both a shock and fire hazard at the conduit.
My post was based on a system with a grounded conductor that is in good condition. If there is a high resistance connection in the parallel path (conduit) more current will flow on the grounded conductor. The only voltage to drive the current through the poor conduit connection will be the voltage drop on the grounded conductor. The voltage drop across the poor conduit connection cannot exceed that of the grounded conductor itself. Of course if the neutral has a problem we can have both a shock and fire hazard at the conduit.
Seriously - I am on the fence of whether it is 'safer' or not :wink: (My ealier post mostly in jest.) - but it does make a good 'back-up' (if well connected) for not burning the place down via your electric blanket - or by the conduit most likely outside that may shock the bejesus out of you when you go to shut it all off. Both are a bad time.....I would rather have the building go "Hi/Low" immediately rather then have a conduit / enclosures start carrying the imbalance until something else fails.