How does one go about determining the fuse size required for protecting control circuit wiring?

I have A vendor supplied contactor with a 460V coil. Coil gets its power from the line side of the but has no protection.

Only protection in the entire circuit is a 25 amp breaker 400 ft from the equipment.

Thanks
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
How does one go about determining the fuse size required for protecting control circuit wiring?

I have A vendor supplied contactor with a 460V coil. Coil gets its power from the line side of the but has no protection.

Only protection in the entire circuit is a 25 amp breaker 400 ft from the equipment.

Thanks

if the wire is #10 than a 25 Amp breaker is sufficient to protect the wiring.
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
How does one go about determining the fuse size required for protecting control circuit wiring?

I have A vendor supplied contactor with a 460V coil. Coil gets its power from the line side of the but has no protection.

Only protection in the entire circuit is a 25 amp breaker 400 ft from the equipment.

Thanks

What size is the control wiring?


SceneryDriver
 

nizak

Senior Member
The control wiring in the assembled enclosure is 16 gauge Cu.
Input power from disconnect for motor is #10thhn.

Push button control and associated wiring for indicator lights etc is all 16
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
The control wiring in the assembled enclosure is 16 gauge Cu.
Input power from disconnect for motor is #10thhn.

Push button control and associated wiring for indicator lights etc is all 16

That seems like it complies with T430.72, Column B.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Compliant or not, we always add fusing to the control circuit wiring. Class CC fuses.

It prevents damage to the PBs and holding contacts when the coil takes a dive.

And to that point, most control circuit devices are going to be rated for 10A continuous, which is why I usually use a 10A CC time delay fuse. That’s not a guarantee though, you really need to double check. Some cheaper stuff is rated for less.
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
using an OCPD to protect a PB or other device is not a code requirement though.

"Not all good ideas are code-enforceable." The fuses are cheap insurance, code-required or not. I'd certainly put them in.