FYI you all are probably aware but UL 508 is not what is was 10 years ago, for over 30 years, significant efforts toward Euro/IEC and North American harmonization have been underway and that train is not stopping. The June 26, 2025, revisions to UL 508A align UL standards even more with the Euro/IEC framework; specifically, UL now recognizes UL 60947-4-1 alongside UL 508 as an acceptable standard for motor controllers. The new version has welcome increased flexibility for electronic devices, disconnecting means, and e-stops. Class 2 circuits can now be powered by sources certified to UL 508, UL 61010-2-201, or UL 61800-5-1.
However, this increased compatibility does not mean one can use random unlisted components and still classify the assembly as a certified control panel. But it might mean more components can get 'recognized', especially if you look into CSA-us or ETL.
It is pretty cool to see how representatives from UL / ETL / CSA now sit on various IEC committees (and vice versa).
You probably notice UL 60947 is replacing many current requirements in UL 508 for several types of industrial control equipment. Additionally, with the rise of VFD's making a regions utility line frequency irrelevant, the 2026 NEC now recognizes 416/240V as a 'standard' voltage (but sadly article 430 lacks a 416V motor table like 508A has Table 50.1)
Ultimately, these changes offer tons of flexibility to design one control panel/process line for both the European and North American markets soon you can design one system for Oregon, Tennessee, Kentucky, and or Estonia, France or Italy .. and so on at a huge cost savings.
But keeping the components sorted is still evolving.