I have a 24VDC 40A power supply with a 40A load side mini breaker feeding other mini breakers.
My initial thought was to daisy chain the breakers with 8awg wire but after some investigation, I realized that the breakers are only rated for (2) 10awg wires.
My question is, am I able to split up the load as shown in the attached example?
I was told I could but I have doubts as I always thought the breaker size cannot exceed the ampacity of the wire.
Thanks in advance.