Control panel

Status
Not open for further replies.

lilsparky

Member
Location
Madison, Al
Hi everyone, it's been awhile since I last posted.

I'm working on a job where the metering components in different facilities are being upgraded. The electrical contractor installed a control panel that contains some computer equipment at one of the facilities. They fed the control panel from an existing 120v receptacle. They didn't install a plug, they hardwired it to the back of the recptacle. I believe this is a code violation and am trying to pin point which code it violates.

I believe the code doesnot allow a dedicated control panel (containing electronic stuff) to be connected to a convenience outlet via hard wire. I have looked at art. 409 Industrial Control panels and art. 210 branch circuits but don't seem to find what I believe is the smoking gun.

Can someone hellp?

Thanks!
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I don't see any violation there...unless the panel load exceeded 50% of the branch circuit rating (assuming a 15A or 20A branch circuit) per 210.23(A)(2).
 

Ranger86

Member
Location
Las Vegas, NV
I think that it would be in the best interest of the building owner to have a dedicated circuit but I don't think that this is a violation. Is this electronic equipment related to any "Life Safety" equipment?
 

lilsparky

Member
Location
Madison, Al
No, it's not tied to any "life safety" equipment. The control panel controls just the water, gas and Emon/Dmon Electric meter. Hmmm I guess I'm suprised. Well thanks for your help, I'll back down lol!!
 