Jacob Kirby
Member
- Location
 - Hudson, WI
 
- Occupation
 - Electrical Engineer
 
I need some guidance for installation of control panels in a Class II Div 2 area. 
As far as I can tell UL508a, UL698a, and UL1203 do not explicitly state they are for use in C2D2 environments. I'm unsure which standard should apply.
Can I just mount a normal UL508a panel in this area? Or do I need to follow UL698a with intrinsic extensions to the C2D2 area? Is there another standard that applies in this situation that I am not aware of?
I get that the enclosure will need to be NEMA Type 12 but that is all that I have solidly found within UL or NEC.
	
		
			
		
		
	
				
			As far as I can tell UL508a, UL698a, and UL1203 do not explicitly state they are for use in C2D2 environments. I'm unsure which standard should apply.
Can I just mount a normal UL508a panel in this area? Or do I need to follow UL698a with intrinsic extensions to the C2D2 area? Is there another standard that applies in this situation that I am not aware of?
I get that the enclosure will need to be NEMA Type 12 but that is all that I have solidly found within UL or NEC.
				