Control Panels in C2D2 Environments

Status
Not open for further replies.

Jacob Kirby

Member
Location
Hudson, WI
Occupation
Electrical Engineer
I need some guidance for installation of control panels in a Class II Div 2 area.

As far as I can tell UL508a, UL698a, and UL1203 do not explicitly state they are for use in C2D2 environments. I'm unsure which standard should apply.

Can I just mount a normal UL508a panel in this area? Or do I need to follow UL698a with intrinsic extensions to the C2D2 area? Is there another standard that applies in this situation that I am not aware of?

I get that the enclosure will need to be NEMA Type 12 but that is all that I have solidly found within UL or NEC.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You have to comply with the requirements found in Article 501 of the NEC. What exactly is in the control panel? Any arc producing contacts will require the use of an NEMA 7 enclosure.
 