Controls in the grounded side

Status
Not open for further replies.

ronaldrc

Senior Member
Location
Tennessee
Re: Controls in the grounded side

Bennie

Don't take what I said about giving me a hard time to serious. I meant in the joking way thats part of the pleasure of posting on these sites.

Ronald ;)
 

ronaldrc

Senior Member
Location
Tennessee
Re: Controls in the grounded side

Bennie thats a good point about the 480 looking like a closed circuit I have never witnessed it myself but do see how it could do that and the motor would not drop out.

Ronald :)
 

bennie

Esteemed Member
Re: Controls in the grounded side

The only time I had this happen was on a water pump for irrigation. The pump starter was interlocked with a permit, or not permit, level switch.

We burnt out a motor when it kept running after water level dropped too low.

The pump was about 150 feet from the level switch, with the conductors firmly together in a cable assembly.

When I changed the control voltage to 240 it performed perfectly.
 

Ed MacLaren

Senior Member
Re: Controls in the grounded side

Ronald et al,
But like ED said its not required untill the va exceeds 1000 va.
That is not what I said.

I said that all control transformer secondaries are required to be grounded except those that meet all of the following conditions.
a. the primary is not over 1000V, and
b. there is qualified maintenance and supervision, and
c. a requirement for control power continuity exists, and
d. ground detectors are installed on the control system.

I also said -
Control transformers up to 1 kva can have the secondary grounded to the control enclosure's equipment grounding conductor.
When the control transformer exceeds 1000 va, then the grounding conductor would have to run to a fully qualified grounding electrode, instead of just to the control enclosure.

This was my interpretation of the '96 NEC rules on the subject. Are you saying that there have been changes?

P.S. - See also ECM Article at http://www.ecmweb.com/ar/electric_code_applies_internal/
Ed

[ August 26, 2003, 10:23 PM: Message edited by: Ed MacLaren ]
 

hillbilly

Senior Member
Re: Controls in the grounded side

Bennie, I'm humbled by your grasp of Electrodynamics. This kind of stuff isn't learned in school.
 

ronaldrc

Senior Member
Location
Tennessee
Re: Controls in the grounded side

ED? don't that mean the same thing I'm sorry take that back I apologize.If I read it wrong. :)

[ August 27, 2003, 12:10 PM: Message edited by: ronaldrc ]
 