What do you think about a swap out a conventional to addressable FACP? :-? I've seen it done in this manner before. I saw it in public housing in Lowell, MA and other public housing projects, but I haven't done it personally.
I am using Silent Knight IFP-1000 (5820XL). I will be using the SD500-MIM (mini input modules) to monitor the sprinkler zones.
I realize the tampers should be separated out but, it was found to be permissible by the AHJ to leave the zones as is, along as any zone that would need to be repaired/replaced at a later date would become fully addressable. The current panel is on its way out, but, not dead, and no one is mandating the change, yet. The owner realized proactive is better than reactive. (yea that's unusual, but refreshing)
I will use a SD-500-SDM (smoke detector modules) to monitor the existing two wire smoke/pull station zones.
Technically the SDM's are for smokes or a conventional two wire circuit, not necessarily mixed devices.
So what do you think